Hello all,
Have a 100 watt quantar being installed in a generated building. Would like to put a ups in line to keep the AC clean and to pick up the lag between loss of AC and generator.
What are you guys using? Would like a rack mount APC unit is possible.
Thanks, Rob
Happy 4th
Quantar and UPS
Moderator: Queue Moderator
Re: Quantar and UPS
I would use a 1000 VA UPS. I use the APC SmartUPS 1000 model (SUA1000).
1000 watts sounds a bit big, but I have found that 500 VA units are only rated at around 300 watts. I have had some that fold back on high in-rush current.
1000 watts sounds a bit big, but I have found that 500 VA units are only rated at around 300 watts. I have had some that fold back on high in-rush current.
- N4DES
- was KS4VT
- Posts: 1234
- Joined: Thu Dec 25, 2003 7:59 am
- What radios do you own?: APX,XTS2500,XTL2500,XTL1500
Re: Quantar and UPS
I have 2 configured the same way and the 1000VA's have no problem holding the load for a minute or more while the generators get their acts together.RFguy wrote:I would use a 1000 VA UPS. I use the APC SmartUPS 1000 model (SUA1000).
1000 watts sounds a bit big, but I have found that 500 VA units are only rated at around 300 watts. I have had some that fold back on high in-rush current.