BTU figures for Motorola Repeaters
Does anyone have has the BTU/HR figures for the "typical" Motorola repeaters? IE: MTR2000 100W UHF 1160 BTU/HR
I have googled it to death & come up empty for the quantar & STR3000
Martin
I have googled it to death & come up empty for the quantar & STR3000
Martin
Just out of curiosity, why would one need to know this? I assume that you are factoring this in for HVAC system design for use in a shelter.
If my assumption's correct, knowing the heat release numbers for a similar piece of equipment could be used in modified form for estimation purposes while being safely conservative. (BTU of other unit x 2). Also, if this is actually a published number, at what duty cycle of transmit is this heat number at?
If my assumption's correct, knowing the heat release numbers for a similar piece of equipment could be used in modified form for estimation purposes while being safely conservative. (BTU of other unit x 2). Also, if this is actually a published number, at what duty cycle of transmit is this heat number at?
-
- Batboard $upporter
- Posts: 502
- Joined: Fri Dec 19, 2003 5:33 pm
Jim,jim wrote:Just out of curiosity, why would one need to know this? I assume that you are factoring this in for HVAC system design for use in a shelter.
If my assumption's correct, knowing the heat release numbers for a similar piece of equipment could be used in modified form for estimation purposes while being safely conservative. (BTU of other unit x 2). Also, if this is actually a published number, at what duty cycle of transmit is this heat number at?
It is for a shelter HVAC calculation. As for the duty cycle 100%, CCS.
I would go for conservative engineering of the HVAC system, but also want to avoid short-cycling the units.
Martin
A 110W Quantar requires about 600W of power in, which means that about 400-500 watts of power have to be dissipated via cooling. According to the Glover "Pocket Reference," one watt is equal to about 3.4 btu/hr. So figure on the order of 1,500 btu/hr. cooling load on your equipment environmental system.
Good idea. There is a Cingular shelter at our FH. The thing must turn on and off 2 or three times in one minute. I don't know how it hasn't crapped out yet but it is annoying as hell to listen to.spareparts wrote:..., but also want to avoid short-cycling the units.
Martin
"I'll eat you like a plate of bacon and eggs in the morning. "
- Some loser on rr.com
eBay at it's finest:
Me: "What exactly is a 900Mhz UHF CB?"
Them: "A very nice CB at 900Mhz speed!"

- Some loser on rr.com
eBay at it's finest:
Me: "What exactly is a 900Mhz UHF CB?"
Them: "A very nice CB at 900Mhz speed!"

-
- Batboard $upporter
- Posts: 502
- Joined: Fri Dec 19, 2003 5:33 pm
To be honest, I'm cheap (as hell) and do not want to waste the electricity starting the HVAC compressors multiple times. And as you inferrred, making the unit crap out waay before it's time.nmfire10 wrote:Good idea. There is a Cingular shelter at our FH. The thing must turn on and off 2 or three times in one minute. I don't know how it hasn't crapped out yet but it is annoying as hell to listen to.spareparts wrote:..., but also want to avoid short-cycling the units.
Martin
Martin
[quote="nmfire10"][quote="spareparts"]..., but also want to avoid short-cycling the units.
Martin[/quote]
Good idea. There is a Cingular shelter at our FH. The thing must turn on and off 2 or three times in one minute. I don't know how it hasn't crapped out yet but it is annoying as hell to listen to.[/quote]
Sounds like your talking about one of the wall hung air units on the typical concrete shelters. In the winter time the fan outdoors will short cycle. The compressor is probably running steady while this is going on. During the cold weather, it is normal for the outside condensor fan to come on and off like your descibing. As long as the compressor isn't doin't that.
Jim
Martin[/quote]
Good idea. There is a Cingular shelter at our FH. The thing must turn on and off 2 or three times in one minute. I don't know how it hasn't crapped out yet but it is annoying as hell to listen to.[/quote]
Sounds like your talking about one of the wall hung air units on the typical concrete shelters. In the winter time the fan outdoors will short cycle. The compressor is probably running steady while this is going on. During the cold weather, it is normal for the outside condensor fan to come on and off like your descibing. As long as the compressor isn't doin't that.
Jim
- psapengineer
- Posts: 175
- Joined: Thu Oct 07, 2004 10:00 am
Don't over or Under Size
Watt's don't convert exactly; it's watt-hours that converts to BTU. So, if your load is constant, the load in watts just happens to be the watt-hours.
Yes,
1 Watt Hour = 3.41 BTU
Then, in cooling tons:
1 Ton Cooling = 12,000 BTU / hr.
You'll also need to add in a factor for the temprature rise for the outdoor heat coming in through the walls and roof through the insulation. This is ofte a big number.
Don't oversize or undersize the unit. If you undersize, of course, it can't keep up, if you undersize it can cause the unit to short cycle or cause the coils to freeze up. It's a delicate balance.
Good Luck, Bob
Yes,
1 Watt Hour = 3.41 BTU
Then, in cooling tons:
1 Ton Cooling = 12,000 BTU / hr.
You'll also need to add in a factor for the temprature rise for the outdoor heat coming in through the walls and roof through the insulation. This is ofte a big number.
Don't oversize or undersize the unit. If you undersize, of course, it can't keep up, if you undersize it can cause the unit to short cycle or cause the coils to freeze up. It's a delicate balance.
Good Luck, Bob
- psapengineer
- Posts: 175
- Joined: Thu Oct 07, 2004 10:00 am
Don't over or Under Size
Watt's don't convert exactly; it's watt-hours that converts to BTU. So, if your load is constant, the load in watts just happens to be the watt-hours.
Yes,
1 Watt Hour = 3.41 BTU
Then, in cooling tons:
1 Ton Cooling = 12,000 BTU / hr.
You'll also need to add in a factor for the temprature rise for the outdoor heat coming in through the walls and roof through the insulation. This is ofte a big number.
Don't oversize or undersize the unit. If you undersize, of course, it can't keep up, if you undersize it can cause the unit to short cycle or cause the coils to freeze up. It's a delicate balance.
Good Luck, Bob
Yes,
1 Watt Hour = 3.41 BTU
Then, in cooling tons:
1 Ton Cooling = 12,000 BTU / hr.
You'll also need to add in a factor for the temprature rise for the outdoor heat coming in through the walls and roof through the insulation. This is ofte a big number.
Don't oversize or undersize the unit. If you undersize, of course, it can't keep up, if you undersize it can cause the unit to short cycle or cause the coils to freeze up. It's a delicate balance.
Good Luck, Bob