BTU figures for Motorola Repeaters

Post by spareparts »

Does anyone have has the BTU/HR figures for the "typical" Motorola repeaters? IE: MTR2000 100W UHF 1160 BTU/HR

I have googled it to death & come up empty for the quantar & STR3000

Martin
User avatar
jim
Posts: 2184
Joined: Sun Sep 09, 2001 4:00 pm

Post by jim »

Just out of curiosity, why would one need to know this? I assume that you are factoring this in for HVAC system design for use in a shelter.


If my assumption's correct, knowing the heat release numbers for a similar piece of equipment could be used in modified form for estimation purposes while being safely conservative. (BTU of other unit x 2). Also, if this is actually a published number, at what duty cycle of transmit is this heat number at?
spareparts
Batboard $upporter
Posts: 502
Joined: Fri Dec 19, 2003 5:33 pm

Post by spareparts »

jim wrote:Just out of curiosity, why would one need to know this? I assume that you are factoring this in for HVAC system design for use in a shelter.

If my assumption's correct, knowing the heat release numbers for a similar piece of equipment could be used in modified form for estimation purposes while being safely conservative. (BTU of other unit x 2). Also, if this is actually a published number, at what duty cycle of transmit is this heat number at?
Jim,
It is for a shelter HVAC calculation. As for the duty cycle 100%, CCS.

I would go for conservative engineering of the HVAC system, but also want to avoid short-cycling the units.

Martin
RKG
Posts: 2629
Joined: Mon Dec 10, 2001 4:00 pm

Post by RKG »

A 110W Quantar requires about 600W of power in, which means that about 400-500 watts of power have to be dissipated via cooling. According to the Glover "Pocket Reference," one watt is equal to about 3.4 btu/hr. So figure on the order of 1,500 btu/hr. cooling load on your equipment environmental system.
User avatar
nmfire10
Batboard $upporter
Posts: 4109
Joined: Sat Jun 29, 2002 4:41 pm

Post by nmfire10 »

spareparts wrote:..., but also want to avoid short-cycling the units.

Martin
Good idea. There is a Cingular shelter at our FH. The thing must turn on and off 2 or three times in one minute. I don't know how it hasn't crapped out yet but it is annoying as hell to listen to.
"I'll eat you like a plate of bacon and eggs in the morning. "
- Some loser on rr.com

eBay at it's finest:
Me: "What exactly is a 900Mhz UHF CB?"
Them: "A very nice CB at 900Mhz speed!"

:-?
spareparts
Batboard $upporter
Posts: 502
Joined: Fri Dec 19, 2003 5:33 pm

Post by spareparts »

nmfire10 wrote:
spareparts wrote:..., but also want to avoid short-cycling the units.

Martin
Good idea. There is a Cingular shelter at our FH. The thing must turn on and off 2 or three times in one minute. I don't know how it hasn't crapped out yet but it is annoying as hell to listen to.
To be honest, I'm cheap (as hell) and do not want to waste the electricity starting the HVAC compressors multiple times. And as you inferrred, making the unit crap out waay before it's time.

Martin
Jim202
Posts: 3610
Joined: Sun Sep 09, 2001 4:00 pm

Post by Jim202 »

[quote="nmfire10"][quote="spareparts"]..., but also want to avoid short-cycling the units.

Martin[/quote]

Good idea. There is a Cingular shelter at our FH. The thing must turn on and off 2 or three times in one minute. I don't know how it hasn't crapped out yet but it is annoying as hell to listen to.[/quote]


Sounds like your talking about one of the wall hung air units on the typical concrete shelters. In the winter time the fan outdoors will short cycle. The compressor is probably running steady while this is going on. During the cold weather, it is normal for the outside condensor fan to come on and off like your descibing. As long as the compressor isn't doin't that.

Jim
User avatar
nmfire10
Batboard $upporter
Posts: 4109
Joined: Sat Jun 29, 2002 4:41 pm

Post by nmfire10 »

Yea, it is one of those big wall hung units on the hut. Thing is, it does this 365 days a year.
"I'll eat you like a plate of bacon and eggs in the morning. "
- Some loser on rr.com

eBay at it's finest:
Me: "What exactly is a 900Mhz UHF CB?"
Them: "A very nice CB at 900Mhz speed!"

:-?
User avatar
psapengineer
Posts: 175
Joined: Thu Oct 07, 2004 10:00 am

Don't over or Under Size

Post by psapengineer »

Watt's don't convert exactly; it's watt-hours that converts to BTU. So, if your load is constant, the load in watts just happens to be the watt-hours.

Yes,

1 Watt Hour = 3.41 BTU

Then, in cooling tons:

1 Ton Cooling = 12,000 BTU / hr.

You'll also need to add in a factor for the temprature rise for the outdoor heat coming in through the walls and roof through the insulation. This is ofte a big number.

Don't oversize or undersize the unit. If you undersize, of course, it can't keep up, if you undersize it can cause the unit to short cycle or cause the coils to freeze up. It's a delicate balance.

Good Luck, Bob
User avatar
psapengineer
Posts: 175
Joined: Thu Oct 07, 2004 10:00 am

Don't over or Under Size

Post by psapengineer »

Watt's don't convert exactly; it's watt-hours that converts to BTU. So, if your load is constant, the load in watts just happens to be the watt-hours.

Yes,

1 Watt Hour = 3.41 BTU

Then, in cooling tons:

1 Ton Cooling = 12,000 BTU / hr.

You'll also need to add in a factor for the temprature rise for the outdoor heat coming in through the walls and roof through the insulation. This is ofte a big number.

Don't oversize or undersize the unit. If you undersize, of course, it can't keep up, if you undersize it can cause the unit to short cycle or cause the coils to freeze up. It's a delicate balance.

Good Luck, Bob